[util] East Tower Generator Test Notice

Jason Tarantino TarantiJ at upstate.edu
Fri May 1 08:08:40 EDT 2026


TO:                  Department Heads, Department Chairmen & Hospital Administration
DATE:             May 2026
SUBJECT:      Generator Test: East Tower
The next monthly test is scheduled for Tuesday, May 19, 2026.
THE EAST TOWER GENERATOR TEST PROCEDURES ARE AS FOLLOWS:
•      The test will be announced over the paging system fifteen minutes prior to the test (5:00AM).
•      The emergency generators will be started between 5:00AM and 5:05AM and used as the source for the emergency power feed for approximately 60 minutes.
•      Emergency power will be switched back to the electrical feed between 6:35AM and 6:45AM when the generators are turned off.
•      Completion of the test will be announced over the paging system.
•      Users of emergency power will notice a series of sequential blinks at the beginning of the East Tower test (one per electrical zone) as each of the 14
emergency power switches are engaged.  At the end of the test, all areas will blink (yellow) as the switches return their respective areas to normal power.
•      Elevators in the East Tower may stop and start during power transition.
If an unavoidable emergency arises close to the time that the emergency generator test is scheduled and you feel that a brief power interruption would be detrimental to patient care, immediately contact the Maintenance Operations Center at 4-4230.
The test, although intended to simulate an actual power outage, has been modified to keep the disruption to Hospital services at a minimum.  If an actual power outage occurs, the electrical circuits supported by the generator will be without power
for 5 to 10 seconds except for those areas which have their own uninterruptible power supplies.  Our recent experience suggests that a real power outage can be expected once a year.  If you have equipment, processes, etc. that cannot cope with a power outage of this duration, your department should consider installing uninterruptible power supplies (UPS's).
If you have any questions or concerns regarding the test or the emergency power system, please feel free to contact Marc Dingle, Electrical Facilities Manager at  4-8923 or 680-323-1819.
Your continued cooperation in completing the code mandated emergency diesel generator test is greatly appreciated.
Thank you.
Reviewed 3-23-21



Best regards,

Jason Tarantino
Administrative Assistant Trainee 2
Physical Plant – Maintenance Operations Center
Upstate Medical University
Room 1806
📞 315-464-4230

Tough times don’t last, but tough people do.
— Robert H. Schuller

[image]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.upstate.edu/pipermail/uh-utility/attachments/20260501/73d54b53/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-image.png
Type: image/png
Size: 6554 bytes
Desc: Outlook-image.png
URL: <http://lists.upstate.edu/pipermail/uh-utility/attachments/20260501/73d54b53/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: East Tower Generator Test Notice.pdf
Type: application/pdf
Size: 171445 bytes
Desc: East Tower Generator Test Notice.pdf
URL: <http://lists.upstate.edu/pipermail/uh-utility/attachments/20260501/73d54b53/attachment.pdf>


More information about the Uh-utility mailing list