[util] UH and Gamma Knife Generator Test Notice

Kimberly J. Austin AustinK at upstate.edu
Mon Nov 1 12:03:27 EDT 2021


TO:                        Department Heads
Department Chairmen
Hospital Administration


DATE:                   November 2021

SUBJECT:        Generator and Fire Service Recall Test: University Hospital and Gamma Knife


The next monthly test is scheduled for Wednesday, November 17, 2021.


The monthly tests will affect those areas with electrical outlets and systems connected to the emergency generator in University Hospital.

THE UNIVERSITY HOSPITAL and GAMMA KNIFE TEST PROCEDURE IS AS FOLLOWS:

1.             The test will be announced over the paging system prior to the test.

2.             Emergency generators will be started between 5:00 a.m. and 5:05 a.m., and used as the source for the emergency power feed for approximately 30 minutes.

3.                   Emergency power will be switched back to the electrical feed between 5:30 a.m. and 5:35 a.m. and the generators turned off.

4.             Completion of the test will be announced over the paging system.


5              Users of the emergency power will notice a blink at the beginning and end of the test.  Activities which can be adversely affected by even a momentary loss of power should not be scheduled or conducted during this time.


Over










Monthly Diesel Generator Tests

Page 2







If an unavoidable emergency arises close to the time that the emergency generator test is scheduled and you feel that a brief power interruption would be detrimental to patient care, immediately contact the Maintenance Operations Center (4-4230).


The test, although intended to simulate an actual power outage, has been modified to keep the disruption to services at a minimum.  If an actual power outage occurs, the electrical circuits supported by the generator will be without power for 5 to 10 seconds with the exception of those areas which have their own uninterruptible power supplies (OR's, etc.)  Our recent experience suggests that a real power outage can be expected once a year.  If you have equipment, processes, etc. that cannot cope with a power outage of this duration, your department should consider installing uninterruptible power supplies (UPS's).

If you have any questions or concerns regarding the test or the emergency power system, please feel free to contact Aaron Petty, Facilities Electrical Manager, Physical Plant at extension 47386.

Your continued cooperation in completing the code mandated emergency diesel generator test is greatly appreciated.


Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.upstate.edu/pipermail/gamma-utility/attachments/20211101/1ba004d2/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 166 bytes
Desc: image001.png
URL: <http://lists.upstate.edu/pipermail/gamma-utility/attachments/20211101/1ba004d2/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: UH and Gamma Knife Generator Test Notice .doc
Type: application/msword
Size: 33280 bytes
Desc: UH and Gamma Knife Generator Test Notice .doc
URL: <http://lists.upstate.edu/pipermail/gamma-utility/attachments/20211101/1ba004d2/attachment.doc>


More information about the Gamma-utility mailing list